• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

2018 NJ IBC - 3" threshold for weather on residential balcony in mixed use building??

nickedemus

Registered User
Joined
Dec 16, 2020
Messages
42
Location
New Jersey
We have a small mixed-use building with 2 retail units on the ground floor, 3 commercial units on the second floor, and three residential units on the third floor. The residential units are not required to be accessible.

Each residential unit has a door opening onto a private terrace. We'd like to have a 3" step down from the residential units to prevent rain and snow from running from the terrace into the residence.

3" doesn't meet ADA/ICC A117.1 threshold requirements, and it's lower than the 4" minimum tread height for a step. But for some reason, I think it's ok....

Is there anywhere in the code that permits a "weather threshold?"

Or is this a non-issue because the units are not required to be accessible, and the terraces are not a part of the egress path?
 
If the units are not required to be accessible, then ANSI A117.1 does not apply.

Refer to Section 1003.5, Exception 1 (2018 IBC), or Section 1010.1.4, Exception 2 (2021 IBC), regarding step height.
 