I'm working on a public housing project in San Jose and am looking for some clarification and/or history on 2019 CBC 11B-205.1 Exception 9.
In residential dwelling units with mobility features where receptacles are provided in a kitchen at a corner work surface, one receptacle shall be located 36 inches from either wall at the inside corner.
Searching through the history of the 2019 versions, it appears that was added as an amendment in 2020 after the 2019 CBC was initially published.
Does anyone know why the DSA decided to add an absolute dimension of 36"? I assume they are trying to align themselves more closely with the FHA but the FHA allows for an outlet to be 36" minimum from the corner. I know the DSA and Ida Clair are fully aware that absolute dimensions create liabilities so I find this shocking and they probably have a good reason for it.
An outlet less than 36" from the corner is definitely not accessible but requiring an outlet to be 36" absolute limits the accessibility of the outlet when one could be located 42" or 48" from the corner and be more accessible.
The HCD fails to even mention an outlet needing to be 36", minimum or absolute, from a kitchen corner in CBC 11A when they should be the forefront of aligning themselves with the FHA anyways. The DSA was probably annoyed that they don't mention this too. I'm kind of ranting at this point though.
Thank you for your help.
In residential dwelling units with mobility features where receptacles are provided in a kitchen at a corner work surface, one receptacle shall be located 36 inches from either wall at the inside corner.
Searching through the history of the 2019 versions, it appears that was added as an amendment in 2020 after the 2019 CBC was initially published.
Does anyone know why the DSA decided to add an absolute dimension of 36"? I assume they are trying to align themselves more closely with the FHA but the FHA allows for an outlet to be 36" minimum from the corner. I know the DSA and Ida Clair are fully aware that absolute dimensions create liabilities so I find this shocking and they probably have a good reason for it.
An outlet less than 36" from the corner is definitely not accessible but requiring an outlet to be 36" absolute limits the accessibility of the outlet when one could be located 42" or 48" from the corner and be more accessible.
The HCD fails to even mention an outlet needing to be 36", minimum or absolute, from a kitchen corner in CBC 11A when they should be the forefront of aligning themselves with the FHA anyways. The DSA was probably annoyed that they don't mention this too. I'm kind of ranting at this point though.
Thank you for your help.