I appreciate the response Greg. I think it’s the existing load time 125% though. It doesn’t say that for the new load, which is what I’m trying to figure out.
		
		
	 
Article 220 (in 2026 NEC, it's Article 120) basically never discusses continuous vs non-continuous.  The output of the article is just a number called "load."  However, other articles refer to the continuous load vs the non-continuous load, so you need a procedure to determine how the load value from Article 220 is broken down into continuous vs non-continuous components.  I would say you have to trace the individual inputs to the computation, grouping them into continuous vs non-continuous, and then see how much of the final load value is attributable to the continuous input load values.  [And in some case it's not clear  how to do that, e.g. 220.82].
In particular if a feeder is protected by a non-100% rated breaker, it needs to be sized at a minimum termination ampacity (not wire ampacity) of 125% times the continuous portion of the load plus 100% times the non-continuous portion of the load.  So as an example, suppose your 220.87 maximum demand comes out to 110A.  You are going to add another 80A of load, of which 60A is continuous and 20A is non-continuous.  Your new load is 125% * 110 + 80A = 218A, of which 60A is continuous.  I'm going to say that since the maximum demand already gets a 125% factor to be converted into a load, you don't have to consider any of that load to be continuous (although that is not actually spelled out).
So if your feeder is protected by a non-100% rated breaker, that breaker would need to be at least 125% * 60A + 158A = 233A, or 250A in practice.  233A is also the minimum termination ampacity (that's the column entry in the ampacity table for your termination temperature rating, without any adjustment or correction).  Your minimum wire ampacity (after adjustment and correction, starting with the column for the insulation temperature rating) would be 218A per 215.2, but would be 226A per 240.4(B) since you must use a 250A breaker.
Cheers, Wayne