I'm bringing a 20,000ft² IT building out of the ground, new construction. Inter-system bonding termination required at service?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Thats the issue, cant be where you please.jar546 said:For the $7.92 I paid for an Arlington terminal with cover compliant with 250.94 and they can put it wherever they please.
250.94 Bonding for Other Systems. An intersystem bondingtermination for connecting intersystem bonding conductors
required for other systems shall be provided external
to enclosures at the service equipment or metering
equipment enclosure
I know that. They still have a choice though so wherever the code allows them. In the case of a house. Outside near the meter base or inside nearest the main disconnect.chris kennedy said:Thats the issue, cant be where you please.
No not a Kenny Klampp That is a device designed by an individual in one of you local jurisdiction in MDpeach said:Is this the same thing as a "Kenny Clamp?". What version of NEC?
peach said:Is this the same thing as a "Kenny Clamp?". What version of NEC?