2nd Floor Window above a 1st Floor Roof

StephNow

REGISTERED
Joined
Oct 20, 2009
Messages
75
Location
Home of Larry Holmes
2009 I-Codes, Northeast Pennsylvania...we get sometimes substantial snow here...

Existing two story SFR, owner wants to put a single story addition to the home. The roof on the addition is only going to be 3" below the 2nd floor window. My concern is large snow loads accumulating with the snow and ice building up around the window and siding.

Any codes, thoughts?

Thanks!
 
We see it here all the time on new construction usually 6 to 9 inches above the roof though. One reason for that is to allow enough room to properly seal and flash the window. If this window is existing i would be concerned with how it may have been installed. Most likely it was just set into a bead of caulking and therefore may be a problem with what you described.
 
No codes help I've ever known, just bad design. Here where snow is rare, those window sills and sash get loaded with rain splatter and have a shortened service life.
 
Just a quick question- If there is a surface located outside the window less than 44" below the sill height, would you allow 5.0 SF opening or 5.7 SF? Contractors have told me that some inspectors have allowed the 5.0 if there is a roof 4/12 slope or less or even a deck/balcony located outside the emergency escape and rescue opening. Any comments or thoughts.
 
If it is not a grade floor opening as defined by the IRC, I would say 5.7.

2006 IRC:

GRADE FLOOR OPENING. A window or other opening located such that the sill height of the opening is not more than 44 inches (1118 mm) above or below the finished ground level adjacent to the opening.

R310.1.1 Minimum opening area.

All emergency escape and rescue openings shall have a minimum net clear opening of 5.7 square feet (0.530 m2).

Exception: Grade floor openings shall have a minimum net clear opening of 5 square feet (0.465 m2).

Inspector 102 said:
Just a quick question- If there is a surface located outside the window less than 44" below the sill height, would you allow 5.0 SF opening or 5.7 SF? Contractors have told me that some inspectors have allowed the 5.0 if there is a roof 4/12 slope or less or even a deck/balcony located outside the emergency escape and rescue opening. Any comments or thoughts.
 
nothing to prohibit having a window as you describe. The same snow problem can occur with window wells to a basement bedroom. Would you look at that case the same? As others have mentioned, it's desirable to have as much space as possible to get the proper flashing installed.
 
Did OP say bedrooms?

Are you sure the windows have to be 5.0 or 5.7 S.F.?

Could u have a fixed window on the second floor meeting height to sill requirement?

If its a bedroom would'nt you be required to only have one window meet egress and the others in the room be less S.F?

Agree with Jim Baird, bad design!
 
Last edited by a moderator:
Inspector 102 said:
Just a quick question- If there is a surface located outside the window less than 44" below the sill height, would you allow 5.0 SF opening or 5.7 SF? Contractors have told me that some inspectors have allowed the 5.0 if there is a roof 4/12 slope or less or even a deck/balcony located outside the emergency escape and rescue opening. Any comments or thoughts.
That kind of interp is what they call a "stretcher", to say the least.
 