Does it really matter whether or not there is a clean out within 40'?

Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Yes it is, and all removable trapsKeystone said:The toilet is considered a cleanout
Contractor was concerned about the holes bored for the 3" pipe so he was being cautiousMsradell said:What's with the 1/2" particleboard sandwiching the joists?
45 degrees or is it 135 degrees?A cleanout is required for a change of direction greater than 45 degrees
Wow that is a sifnificant differance between the IPC and UPC.WSH1852 said:IPC 2012708.3.3 Changes of direction. Cleanouts shall be installed at each change of direction greater than 45 degrees (0.79 rad) in the building sewer, building drain and horizontal waste or soil lines. Where more than one change of direction occurs in a run of piping, only one cleanout shall be required for each 40 feet (12 192 mm) of developed length of the drainage piping.