Previewing a set of apartments under 2012 IBC; 3 story, four R2 dwelling units per floor served by a single open access stairway. Travel distance under 125 ft. per Table 1021.2(1) The configeration are 4 sets of towers or buildings under one roof with open breezeways in-between.
The stairway is surrounded with exterior walls on 3 sides and access from outside the dwelling units through an open breezeway between buildings.
Is NFPA 13 required throughout the buildings and exterior stairway with draft curtains even though it's outside?
1009.3 Exit access stairways.
Floor openings between stories created by exit access stairways shall be enclosed.
Exceptions:
1. In other than Group I-2 and I-3 occupancies, exit access stairways that serve, or atmospherically communicate between, only two stories are not required to be enclosed.
2. Exit access stairways serving and contained within a single residential dwelling unit or sleeping unit in Group R-1, R-2 or R-3 occupancies are not required to be enclosed.
3. In buildings with only Group B or M occupancies, exit access stairway openings are not required to be enclosed provided that the building is equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1, the area of the floor opening between stories does not exceed twice the horizontal projected area of the exit access stairway, and the opening is protected by a draft curtain and closely spaced sprinklers in accordance with NFPA 13.
4. In other than Group B and M occupancies, exit access stairway openings are not required to be enclosed provided that the building is equipped throughout with an automatic sprinkler system in accordance with :Next('./icod_ibc_2012_9_par054.htm')'>Section 903.3.1.1, the floor opening does not connect more than four stories, the area of the floor opening between stories does not exceed twice the horizontal projected area of the exit access stairway, and the opening is protected by a draft curtain and closely spaced sprinklers in accordance with NFPA 13.
Francis
The stairway is surrounded with exterior walls on 3 sides and access from outside the dwelling units through an open breezeway between buildings.
Is NFPA 13 required throughout the buildings and exterior stairway with draft curtains even though it's outside?
1009.3 Exit access stairways.
Floor openings between stories created by exit access stairways shall be enclosed.
Exceptions:
1. In other than Group I-2 and I-3 occupancies, exit access stairways that serve, or atmospherically communicate between, only two stories are not required to be enclosed.
2. Exit access stairways serving and contained within a single residential dwelling unit or sleeping unit in Group R-1, R-2 or R-3 occupancies are not required to be enclosed.
3. In buildings with only Group B or M occupancies, exit access stairway openings are not required to be enclosed provided that the building is equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1, the area of the floor opening between stories does not exceed twice the horizontal projected area of the exit access stairway, and the opening is protected by a draft curtain and closely spaced sprinklers in accordance with NFPA 13.
4. In other than Group B and M occupancies, exit access stairway openings are not required to be enclosed provided that the building is equipped throughout with an automatic sprinkler system in accordance with :Next('./icod_ibc_2012_9_par054.htm')'>Section 903.3.1.1, the floor opening does not connect more than four stories, the area of the floor opening between stories does not exceed twice the horizontal projected area of the exit access stairway, and the opening is protected by a draft curtain and closely spaced sprinklers in accordance with NFPA 13.
Francis