• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

310.15(B)(2)(c)

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,055
Location
Somewhere Too Hot & Humid
Anyone else ask for the ambient temperature calculations?

This is a short one but I have had a few that were several hundred feet.

IMAG0092.jpg
 
No commercial electrical guys out there?

Do you do the calc at plan review or do you ask for that info from the electrical engineer that designed it?

I have found out that most EEs are not aware this new section in the 2008 NEC exists.
 
Length of the run has no bearing on any calcs. And it's hard to assist you in any calcs without any information.

Other than that, I would simply build any calcs into my bid. The plans will tell you what is needed, all you need is to design the system on paper, using T310.15(B)(2)© to calculate any temperature 'adder'.
 
But what do you base those calcs on? This is a helpful link to find the design temps in you area from the guys that promote derating to sell larger wire. ;) But I do use this same table for my calcs.

Design temps.

BTW Jeff, do you know where they get those sporty end caps for the uni-strut?
 