Francis Vineyard
An apartment building of Type 3 construction has rooms or closets the are access from the corridor that encloses HVAC equipment that serves the corridor. The rooms or closets have electrical and or communication equipment.
It is permitted to have exposed Romex where not subject to damage in these rooms and other areas of an apartment building including storage areas, parking garage, offices, retail spaces?
Underlined added for emphasis of clarification.
334.10 Uses Permitted. Type NM, Type NMC, and Type
NMS cables shall be permitted to be used in the following:
(1) One- and two-family dwellings and their attached or
detached garages, and their storage buildings.
(2) Multifamily dwellings permitted to be of Types III, IV,
and V construction except as prohibited in 334.12.
(3) Other structures permitted to be of Types III, IV, and V
construction except as prohibited in 334.12. Cables
shall be concealed within walls, floors, or ceilings that
provide a thermal barrier of material that has at least a
15-minute finish rating as identified in listings of firerated
assemblies.
Informational Note No. 1: Types of building construction
and occupancy classifications are defined in NFPA 220-
2009, Standard on Types of Building Construction, or the
applicable building code, or both.
Informational Note No. 2: See Informative Annex E for
determination of building types [NFPA 220, Table 3-1].
(4) Cable trays in structures permitted to be Types III, IV,
or V where the cables are identified for the use.
Informational Note: See 310.15(A)(3) for temperature
limitation of conductors.
(5) Types I and II construction where installed within raceways
permitted to be installed in Types I and II
construction.
assemblies.
construction.