TheCommish
2015 IBC, no applicable local amendments.
Reviewing a major distribution warehouse for permit issuance, very large mezzanine area at least three stairs down to the main floor 36 inched wide. My comment to the designer Stairs x,y,z seem to violate the requirement of 1011.2 44 inch width.
Answer 1011.2 width and capacity. Exception #1 stairway serving an occupant load of less then 50 shall have a width of not less the 36". refer to code analysis sheet, Platforms do not contribute to building or fire area. Only 100 occupants are calculated for the mezzanine perimeter has multiple stairs. There would be less than 50 at each stair.
505.2 Mezzanines. A mezzanine or mezzanines in compliance with Section 505.2 shall be considered a portion of the story below. Such mezzanines shall not contribute to either the building area or number of stories as regulated by Section 503.1. The area of the mezzanine shall be included in determining the fire area. The clear height above and below the mezzanine floor construction shall be not less than 7 feet...
505.2.2 Means of egress. The means of egress for mezzanines shall comply with the applicable provisions of Chapter 10.
1006.1 General. The number of exits or exit access doorways required within the means of egress system shall comply with the provisions of Section 1006.2 for spaces, including mezzanines, and Section 1006.3 for stories.
1006.2 Egress from spaces. Rooms, areas or spaces, including mezzanines, within a story or basement shall be provided with the number of exits or access to exits in accordance with this section.
I agree that the mezzanine does not count to the build area or building height, this has nothing to do with occupant load.
Definition chapter 2 OCCUPANT LOAD. The number of persons for which the means of egress of a building or portion thereof is designed.
Concern/question for the group is the designer allowed to use multiple stairs in the scenario to divide the load (like exit doors) or is the occupant load of 100 counted to a single stair and a second exit off the mezzanine needed?
Thanks
Thanks
