360 degrees of bends in conduit

Maybe the real question should be whether the required wires have been installed and whether the conduit protects those wires.
 
Agree, their at the limit. Your allowed 4-90° (1/4 bends) between pull points. Lower roof has an LB pull point and I assume the roof has a JB pull point and not another 1/4 bend?

You might be able to gig em for 352.30, conduit support if the conduit is 1-inch size or less?

Most of the solar installs her have been in metal conduit.
 
Just trying to get the basis of the section in text, "There shall not not be more than the equivalent of four quarter bends (360 degrees) between pull points (LB)".......I believe this to be compliant, actually, more than compliant. Assuming that the final connection is in a "pull point" or J-Box, the last bend is NOT 90 degrees.
 