Hello All,
I have a question concerning the 2020 NEC Changes in 230.70, 230.71, specifically 230.71(B): Prior to 2020 NEC, a 400A meter Main allowed 2 x 200A Main Breakers in the same cavity/enclosure. According to the 2020 NEC, a change was made which required each 200A Breaker be separated either using a 400A Meter Socket and a 200A disconnect on each side or vertically with a partition. I have a guy that is arguing his "Old Style" 400A Meter Main with the dead front attachment is code compliant. Sorry, I can't insert the pictures like I wanted.
When the dead front removed, there are two 200A breakers in the same cavity/enclosure. There is a dead front attachment (like a "T" bar) from Square D and it does make the two switches into one switch, I get that. However, it does not provide any safety from arc flash or electrocution if the dead front is removed. In my mind and research, safety was/is the point of the code change. Square D is also saying the dead front attachment meets code. I don't see it!
I have found only one thread on here so far with info on this topic. 2020 NEC Changes to 230.71 Service Equipment Disconnecting Means Maximum Number of Disconnects | The Building Code Forum I've inserted this link of a Mike Holt interview which gives support to my point/question.
I will continue to research. Our plan reviewer and I have the same opinion. He's a 40 yr Master Electrician.
I'd like to hear from all of you concerning this matter.
Thank you for reading and anticipated reply!
Have a great weekend!
I have a question concerning the 2020 NEC Changes in 230.70, 230.71, specifically 230.71(B): Prior to 2020 NEC, a 400A meter Main allowed 2 x 200A Main Breakers in the same cavity/enclosure. According to the 2020 NEC, a change was made which required each 200A Breaker be separated either using a 400A Meter Socket and a 200A disconnect on each side or vertically with a partition. I have a guy that is arguing his "Old Style" 400A Meter Main with the dead front attachment is code compliant. Sorry, I can't insert the pictures like I wanted.
When the dead front removed, there are two 200A breakers in the same cavity/enclosure. There is a dead front attachment (like a "T" bar) from Square D and it does make the two switches into one switch, I get that. However, it does not provide any safety from arc flash or electrocution if the dead front is removed. In my mind and research, safety was/is the point of the code change. Square D is also saying the dead front attachment meets code. I don't see it!
I have found only one thread on here so far with info on this topic. 2020 NEC Changes to 230.71 Service Equipment Disconnecting Means Maximum Number of Disconnects | The Building Code Forum I've inserted this link of a Mike Holt interview which gives support to my point/question.
I'd like to hear from all of you concerning this matter.
Thank you for reading and anticipated reply!
Have a great weekend!