Does this section mean that at all corners, they will be sheathed no less than 24" from the corner or as they have refernced method #3 that the min. width of sheathing panel next to an opening could be located within 12.5 feet from the corners as outlined in 602.10.1.
I have a submittal for cont. sheathed home and one corner of the house locates two windows in the corner at about 16" from each corner edge. No more than 65% of the wall height, so a min. of a 24" sheathed panel is required per table 602.10.5. Could they be using the other side of the window opening for the min. of 24" as long as they are within the first 12.5 feet?
Or do they need to provide some shear panel at this corner condition?
It seems that 602.10.6.2 # 1 for single story requires this panel to be a min. of 16" and # 2 for two story condition to be a min. of 24"
Or is this just not allowed under the 16" min. and 24" min. Move the windows outward to these minimums?
I have a submittal for cont. sheathed home and one corner of the house locates two windows in the corner at about 16" from each corner edge. No more than 65% of the wall height, so a min. of a 24" sheathed panel is required per table 602.10.5. Could they be using the other side of the window opening for the min. of 24" as long as they are within the first 12.5 feet?
Or do they need to provide some shear panel at this corner condition?
It seems that 602.10.6.2 # 1 for single story requires this panel to be a min. of 16" and # 2 for two story condition to be a min. of 24"
Or is this just not allowed under the 16" min. and 24" min. Move the windows outward to these minimums?