Hello all,
I purchased a used 710B hood so that I could purchase a fryer for my restaurant. It is specifically an American Hood Systems AVH 23:
https://www.americanhood.com/products/ventless_hoods/ventless_hood.html
I planned on getting it professionally installed with all of the permits. The fire marshal is not having an issue with it, but the building inspector is saying that I need a Type 1 hood for a fryer, and it needs to vent out of the building.
I also know that I will only be able to use UL197 electrical fryers with it as well.
I thought the whole point of these types of hoods were that they are used when you can't vent out of the building?
Is there something that I am missing? Any help would be appreciated.