I recently received a request to accept kraft back insulation in an above ceiling (concealed space), "B" occupancy, Type V-B construction application where the kraft backed insulation is installed 'behind and in substantial contact with the unexposed surface of the ceiling or wall finish.' I was wondering if it was just me, or does the language listed below, suggest that facing exemptions only apply to reflective foil insulation?
(2006 IBC) 719.2.1 Facings. Where such materials are installed in concealed spaces in buildings of Type III, IV, or V construction, the flame spread and smoke-development limitations do not apply to facings, coverings, and layers of reflective foil insulation that are installed behind and in substantial contact with the unexposed surface of the ceiling, wall or floor finish.
(2006 IBC) 719.2.1 Facings. Where such materials are installed in concealed spaces in buildings of Type III, IV, or V construction, the flame spread and smoke-development limitations do not apply to facings, coverings, and layers of reflective foil insulation that are installed behind and in substantial contact with the unexposed surface of the ceiling, wall or floor finish.