907.6.5 Monitoring. Fire alarm systems
mtlogcabin
Big Sky Country
[F] 907.6.5 Monitoring.
Fire alarm systems required by this chapter or by the International Fire Code shall be monitored by an approved supervising station in accordance with NFPA 72.
A local cable/internet provider has been selling and installing modems and internet service to replace the required telephone lines required by NFPA 72 2007 that we are under. I have heard the newer NFPA 72 version has addressed this type of notification system. I am looking for information on what we should be looking for such as battery backup for the modem, is a back up modem required, reporting requirements, acceptance testing requirements ETC. Any info/educational links/material would be greatly appreciated. If it is in NFPA 72 please advise which edition so I can order the correct copy/handbook
no battery back up required as of now,
will need to check nfpa 72 it is in there, but not much info
I think about the same reporting frequency as a cell phone system.
What edition of 72 are you currently under?
The system is montiored by an approved monitoring station??? Even with the internet?
sorry running out of time will give a look at 72 tommorow
you are looking for "Ip datc"
MT,
NFPA 72, 2007 [8.6.4.1 through 8.6.6] all of Chapter 4 still applies to the technology and the newer editions catch up with inclusion of the technology and clears up the Chapter 4 pathway stuff for this technology.
[26.3.1 and Chapter 10] NFPA 72, 2013