• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

A ComCheck Question

glzath

Registered User
Joined
Apr 10, 2013
Messages
44
Location
Wadsworth, Ohio
IECC 2015

Adding on a 2700 SF addition to an existing 50,000 SF manufacturing facility. Approximately 2/3rds of the addition will have new, exterior walls with the remaining 1/3rd using a shared wall with the existing plant. Conditioning of the two spaces will be similar. How would that shared wall be classified in ComCheck (Other:Exterior?) and what "R"/"U" value would I use for that 1/3rd portion?

Thanks
 
The wall in question is common to both areas that are heated? If it is I don't think that you have to enter anything as it is not part of the building envelope anymore. Thoughts?
 
Agreed with jpranch. Any energy modeling software is usually only concerned with surfaces affecting heat loss.
 