Simonsays
- Joined
- Mar 2, 2010
- Messages
- 68
Trying to help a designer comply in a tough situation …
The applicable building code is the 2006 IBC for an existing two story wood frame mixed use building, mercantile on the first floor and two R-3 residences above. There is no existing separation, just a wood floor and wood joists. The project involves modifying the center support of the floor joists by installing a lightweight steel beam, as a column is in the way of proposed mercantile area changes.
Can’t use 3410 as a new unprotected steel beam will make the building less safe per 3410.2.4, IMHO. (It’s the same principle as with new openings in an existing unrated and unsprinklered corridor why you must install new fire-rated doors.)
Can’t substitute an engineered wood beam and use three layers of type X per Table 721.6.2(1) to get the two hour rating as that would violate 721.6.1.1.
The proposed lightweight beam violates 721.5.2.1.2 as its W/D ratio is less than the beam in the approved assembly (U L design N 501).
Is there another, easier, and code-complying path that I am failing to see?