• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Acceptable Electrical Panel Marking

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,096
Location
Somewhere Too Hot & Humid
In this case, the panel labeling is correct for the physical location but the panel cover was apparently knocked out wrong so the electrician put the cover on upside down which then makes the numbers of the panel OCPD list wrong by number.

Would you find this acceptable or write it up as a deficiency under NEC 408.4(A) "Circuit Directory or Circuit Identification"

IMG_2131.JPG IMG_2132.jpg
 
I would cite the violation. Avoidable confusion is never acceptable when controlling electricity.