DTBarch
SAWHORSE
Project: Warehouse Tenant Improvement
Location: Phoenix AZ
Applicable Code: 2012 IBC
Property Description: Existing 33,000sf warehouse space containing 4,000sf office has been vacant for 3 years.
Last Permitted Occupancy: Previous tenant was permitted under occupancy class B/S-1/F-1
New tenant prospect would like to lease the space as-is, with the only permitted alteration being the installation of a paint booth (electrical, mechanical, maybe structural at roof penetration). Same occupancy mix as prior tenant, so no change in occupancy.
Existing office has NO ramp at the entrance, just concrete stairs. Office toilet rooms are mostly non-accessible. There are two mostly accessible toilet rooms in the warehouse, away from the office, which were built in a 2007 permitted T.I.
The cost of the electrical and mechanical hookups for the paint booth is $40,000.
If we apply IBC 3411.7.1, 20% of the cost of alteration is $8k.
Typically, when applying the 20% rule, we start at the exterior and work in. In this case, we know from multiple recent project history, the cost of installing a ramp will be between $20k-$30k . In this case, since providing basic accessibility to the entrance exceeds the 20% threshold, would we then simply skip to the interior and apply improvements up to $8k in the toilet rooms, EDF, etc. Since the AHJ doesn't enforce federal, and the A117.1 Chapter 2 gives all authority of scoping on alterations to the AHJ, which leads us directly back to IBC Chapter 34, are there any other provisions in the code that would force installation of the ramp.
Neither the tenant nor landlord want to be exposed to a $20k-$30k change after the lease is signed, so we're flushing out any exposure up front.
Clearly, there is always inherent exposure to the owner/tenant from the federal side with public and employees, but we're specifically considering immediate exposure related to the building permit.
Thanks in advance for your feedback.
Location: Phoenix AZ
Applicable Code: 2012 IBC
Property Description: Existing 33,000sf warehouse space containing 4,000sf office has been vacant for 3 years.
Last Permitted Occupancy: Previous tenant was permitted under occupancy class B/S-1/F-1
New tenant prospect would like to lease the space as-is, with the only permitted alteration being the installation of a paint booth (electrical, mechanical, maybe structural at roof penetration). Same occupancy mix as prior tenant, so no change in occupancy.
Existing office has NO ramp at the entrance, just concrete stairs. Office toilet rooms are mostly non-accessible. There are two mostly accessible toilet rooms in the warehouse, away from the office, which were built in a 2007 permitted T.I.
The cost of the electrical and mechanical hookups for the paint booth is $40,000.
If we apply IBC 3411.7.1, 20% of the cost of alteration is $8k.
Typically, when applying the 20% rule, we start at the exterior and work in. In this case, we know from multiple recent project history, the cost of installing a ramp will be between $20k-$30k . In this case, since providing basic accessibility to the entrance exceeds the 20% threshold, would we then simply skip to the interior and apply improvements up to $8k in the toilet rooms, EDF, etc. Since the AHJ doesn't enforce federal, and the A117.1 Chapter 2 gives all authority of scoping on alterations to the AHJ, which leads us directly back to IBC Chapter 34, are there any other provisions in the code that would force installation of the ramp.
Neither the tenant nor landlord want to be exposed to a $20k-$30k change after the lease is signed, so we're flushing out any exposure up front.
Clearly, there is always inherent exposure to the owner/tenant from the federal side with public and employees, but we're specifically considering immediate exposure related to the building permit.
Thanks in advance for your feedback.