2. I haven't seen anything regarding amphitheaters or stadiums in their codes. With 188 seats, I should only need 1 ADA space, yes?
You might want to look a little closer at the code
An amphitheater is an Assembly area and a Performance area, both in the code
IlB-206.2.6 Performance areas. Where a circulation path directly connects a performance area to an assembly seating area, an accessibJe route shall directly connect the assembly seating area with the performance area. An accessible route shall be provided from performance areas to ancillary areas or facilities used by performers unless exempted by Section 11B-206.2.3 Exceptions 1 through 7.
11B-221 Assembly areas
11B-221.1 General. Assembly areas shall provide wheelchair spaces, companion seats, and designated aisle seats and semi-ambulant seats complying with Sections 11 B-221 and
11 B-802. In addition, lawn seating shaH comply with Section 11B-221.5.
11B-221.2 Wheelchair spaces. Whee1chair spaces complying with Section 11B-221.2 shall be provided in assembly areas with fixed
11B-221.2.1 Number and location. Whee1chair spaces shall be provided complying with Section 11B-221.2.1.
11B-221.2.1.1 General seating. Wheelchair spaces complying with Section 11B-802.1 shall be provided in accordance with Table 11B-221.2.1.1.
TABLE 118-221.2.1.1
NUMBER OF WHEELCHAIR SPACES IN ASSEMBLY AREAS
NUMBER OF SEATS MINIMUM NUMBER OF REQUIRED WHEELCHAIR SPACES
4 to 25 1
26 to 50 2
51 to 150 4
151 to 300 5
301 to 500 6
501 to 5000 6, plus 1 for each 100, or fraction thereof, between 501 through 5000 5001 and over 46, plus 1 for each 200, or fraction thereof, over 5000
11B-221.2.1.6 Specialty seating areas. In assembly areas, wheelchair spaces shall be provided in each specialty seating area that provides spectators with distinct services or amenities that generally are not
available to other spectators. The number of wheelchair spaces provided in specialty seating areas shall be included in, rather than be in addition to, the total number of wheelchair spaces required by Table 11 B- 221.2.1.1.
11B-221.2.2 Integration. Wheelchair spaces shall be an integral part of the seating plan.
11B-221.2.3 Lines of sight and dispersion. Wheelchair spaces shall provide lines of sight complying with Section 11B-802.2 and shall comply with Section llB-221.2.3.
In providing lines of sight, wheelchair spaces shall be dispersed. Wheelchair spaces shall provide spectators with choices of seating locations and viewing angles that are substantially equivalent to, or better than, the choices of seating locations and viewing angles available to all other spectators. When the number of wheelchair spaces required by Section 11 B-221.2.1 has been met, further dispersion shall not be required. In stadiums, arenas and grandstands, wheelchair spaces shall be dispersed to all levels that include seating served by an accessible route
Also see
11B-221.2.3.1 Horizontal dispersion..
11B-221.2.3.2 Vertical dispersion.
llB-221.2.5 Removable chairs.
llB-221.3 Companion seats.
llB-221.4 Designated aisle seats.
llB-221.S Lawn seating.
llB-221.6 Semi-ambulant seats.