• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

ADA Urinals

north star

Sawhorse
Joined
Oct 19, 2009
Messages
4,596
@ ~ @

Greetings all !

I have a project whereby one A.D.A compliant Restroom is being
installed in small office addition.......This Restroom has one A.D.A.
compliant Toilet, Lavatory & Shower Compartment, and one
non-A.D.A. compliant Urinal.......The applicable Codes are the
2012 I-Codes, including the 2009 A117.1 & the 2010 A.D.A.S.A.D.


Is an A.D.A. compliant urinal "required", or can the Toilet meet the
requirement of providing a compliant accessible fixture ?

May I please request the applicable codes sections.

Thank you !


@ ~ @
 
2012 IBC
1109.2 Toilet and bathing facilities
. Each toilet room and
bathing room shall be accessible. Where a floor level is not
required to be connected by an accessible route, the only toilet
rooms or bathing rooms provided within the facility shall
not be located on the inaccessible floor. At least one of each
type of fixture, element, control or dispenser in each accessible
toilet room and bathing room shall be accessible.
Exceptions:
4. Where no more than one urinal is provided in a toilet
room or bathing room, the urinal is not required to
be accessible.


"Exception 4—The IPC permits urinals to be substituted
for water closets to a maximum of 67 percent in
each toilet room (see Section 419.2 of the IPC).
Exception 4 states that if only one urinal is provided
within a toilet room, that urinal is not required to be
accessible. This situation would typically only occur in
toilet rooms that also had one water closet compartment."

2010 Standards: Titles II and III
213.3 Plumbing Fixtures and Accessories.
Plumbing fixtures and accessories provided in a toilet room or bathing room required to comply with 213.2 shall comply with 213.3.

213.3.1 Toilet Compartments. Where toilet compartments are provided, at least one toilet compartment shall comply with 604.8.1. In addition to the compartment required to comply with 604.8.1, at least one compartment shall comply with 604.8.2 where six or more toilet compartments are provided, or where the combination of urinals and water closets totals six or more fixtures.

213.3.2 Water Closets. Where water closets are provided, at least one shall comply with 604.

213.3.3 Urinals. Where more than one urinal is provided, at least one shall comply with 605.

 
Just in case anyone is wondering, the 2015 ABA Standards, applicable to federal DoD, GSA, and USPS facilities has the same language.

F213.3.3 Urinals. Where more than one urinal is provided, at least one shall comply with 605.
 