I have had some inspectors question whether or not a bathroom can be considered 'similar areas' for requiring AFCI protection.
My opinion is NO, AFCI is not required in bathrooms. The NEC explicitly lists all of the areas and does not say bathrooms. Bathrooms, are however in other areas of the code such as GFCI protection, so it is my opinion that bathrooms were intentionally left off of the AFCI list. What are your thoughts?
210.12(B) Dwelling Units.
All 120-volt, single-phase, 10-, 15-, and 20-ampere branch circuits supplying outlets or devices installed in the following locations shall be protected by any of the means described in 210.12(A)(1) through (A)(6):
My opinion is NO, AFCI is not required in bathrooms. The NEC explicitly lists all of the areas and does not say bathrooms. Bathrooms, are however in other areas of the code such as GFCI protection, so it is my opinion that bathrooms were intentionally left off of the AFCI list. What are your thoughts?
210.12(B) Dwelling Units.
All 120-volt, single-phase, 10-, 15-, and 20-ampere branch circuits supplying outlets or devices installed in the following locations shall be protected by any of the means described in 210.12(A)(1) through (A)(6):
- (1)Kitchens
- (2)Family rooms
- (3)Dining rooms
- (4)Living rooms
- (5)Parlors
- (6)Libraries
- (7)Dens
- (8)Bedrooms
- (9)Sunrooms
- (10)Recreation rooms
- (11)Closets
- (12)Hallways
- (13)Laundry areas
- (14)Similar areas