First off, I appreciate this forum. I've lurked around for years, usually finding whatever answer I was searching for. However, I've now come to a problem/discussion for which I would greatly appreciate the input of Code Officials, Architects or other Engineers. Here is the situation.
We are working on a "complex" in a municipality under 2012 IBC.
There is an existing stall barn for their horses (72'x104' w/ 8' lean-to each side). They plan to construct an enclosed exercise area (80'x150') and a hay barn. They are currently located 10.5' apart. Two open-sided, covered walkways connect the stall barn and exercise area; the hay barn is standalone. The barns are in the middle of a 1700' by 3000' lot. The Code Reviewer sought clarification regarding the separation between the structures.
All construction is VB.
Initially we designed the project considering the separation between structures under table 602 for Group U with x = 10.5 feet. This is apparently incorrect. We should have referenced 705.3 for buildings on the same lot, wherein an imaginary line is constructed between structures, the distance from the exterior wall to this line is the 'x' value. Meaning, as our arrangement sits (with 10.5 feet between buildings) we would actually fall into the 1 hour separation requirement from 5
However, in the exemption of 705.3, two or more buildings may be considered as aggregate parts of one if the total area falls under the values from Chapter 5. And this is where it gets tricky...
Our facility clearly meets all requirements of Appendix C: Group U - Agricultural Buildings. In this Appendix, with surrounding yard distances exceeding 60 feet, we are permitted a one-story unlimited area for these structures (C102.2). So, can I consider the complex as one building with unlimited area under Appendix C meeting all other criteria. I cannot find explicit reference to Appendix C in the building areas table in Chapter 5.
I would like the input from folks on this forum. I just proposed the analysis yesterday afternoon.
UPDATE: The codes department accepted and approved my review within minutes of submittal. Nevertheless, if people have additional comments / insights I would like to hear them. Being educated in code is a critical part of my practice.
We are working on a "complex" in a municipality under 2012 IBC.
There is an existing stall barn for their horses (72'x104' w/ 8' lean-to each side). They plan to construct an enclosed exercise area (80'x150') and a hay barn. They are currently located 10.5' apart. Two open-sided, covered walkways connect the stall barn and exercise area; the hay barn is standalone. The barns are in the middle of a 1700' by 3000' lot. The Code Reviewer sought clarification regarding the separation between the structures.
All construction is VB.
Initially we designed the project considering the separation between structures under table 602 for Group U with x = 10.5 feet. This is apparently incorrect. We should have referenced 705.3 for buildings on the same lot, wherein an imaginary line is constructed between structures, the distance from the exterior wall to this line is the 'x' value. Meaning, as our arrangement sits (with 10.5 feet between buildings) we would actually fall into the 1 hour separation requirement from 5
However, in the exemption of 705.3, two or more buildings may be considered as aggregate parts of one if the total area falls under the values from Chapter 5. And this is where it gets tricky...
Our facility clearly meets all requirements of Appendix C: Group U - Agricultural Buildings. In this Appendix, with surrounding yard distances exceeding 60 feet, we are permitted a one-story unlimited area for these structures (C102.2). So, can I consider the complex as one building with unlimited area under Appendix C meeting all other criteria. I cannot find explicit reference to Appendix C in the building areas table in Chapter 5.
I would like the input from folks on this forum. I just proposed the analysis yesterday afternoon.
UPDATE: The codes department accepted and approved my review within minutes of submittal. Nevertheless, if people have additional comments / insights I would like to hear them. Being educated in code is a critical part of my practice.