How is everyone interpreting 2005 NEC 680.26, Equipotential Bonding, when it comes to above ground pools that have a metal wall and vinyl liner?

The requirements seem to be geared more towards inground pools.

Do you require a bonding grid around the pool?
 
No, we feel like the metal wall of a vinyl pool setting on the ground is the bonding grid. All metal parts of the pool must be bonded.

Here is a portion of the document.....

We base our interpretation on #2

To properly mask stray voltage, an equipotential (stray voltage)

grid must extend under walking surfaces for 3 ft horizontally

from the water, Figure 680-23. The equipotential (stray voltage)

grid must be formed from one or more of the following:

(1) Structural Reinforcing Steel. Structural reinforcing steel of

the concrete permanently installed pool, outdoor spa, or outdoor

hot tub.

(2) Bolted or Welded Metal Pools. The walls of a bolted or

welded metal permanently installed pool, outdoor spa, or outdoor

hot tub.

(3) Other Methods. The equipotential (stray voltage) grid can

be constructed as specified in (a) through © below.

Here is the publication on grounding/bonding of pools. Look at page 26 for your situation.

Mike Holt Pool Document

Are we doing wrong???????
 
Section 680.26 applies to ALL permanently installed pools (680.20), outdoor (680.42) and indoor (680.43) spas and hot tubs, fountains common to a pool (680.50), and permanently installed therapeutic pools (680.61).

Section 680.26 of the 2005 NEC is poorly arranged and written. The reformatted section in the 2008 NEC is much better organized.
 