Had an application come in for an industrial building. >600m2 (>6000 ft2 for you murricans).
Canadian Code requires this floor are to have more than one exit (outward swinging door).
Designer pushing back, with the declaration the "actual" area will be far less because sand/salt will be stored in the structure, and it's low human occupancy.
Received the "We've done a dozen of these in the province, never had to do this anywhere else" line.
The way I see it, the floor area is clearly defined as outside wall to outside wall - independent of what's inside. The structure requires two exits. It exceeds the 200m2 limit under Part 3 for one exit, simple and easy.
Part 2, which deals with farm buildings (low human occupancy) has the same criteria, btw., so "low human occupancy" doesn't act as the get out of the second exit free card, even if used as a reference/alternative solution. (And it's not a farm building in any event.)
Thoughts?
Canadian Code requires this floor are to have more than one exit (outward swinging door).
Designer pushing back, with the declaration the "actual" area will be far less because sand/salt will be stored in the structure, and it's low human occupancy.
Received the "We've done a dozen of these in the province, never had to do this anywhere else" line.
The way I see it, the floor area is clearly defined as outside wall to outside wall - independent of what's inside. The structure requires two exits. It exceeds the 200m2 limit under Part 3 for one exit, simple and easy.
Part 2, which deals with farm buildings (low human occupancy) has the same criteria, btw., so "low human occupancy" doesn't act as the get out of the second exit free card, even if used as a reference/alternative solution. (And it's not a farm building in any event.)
Thoughts?