In exception #2 below, is there anything that requires the ramp to connect to a different floor level?
I know of a developer who wants to provide an elevator for normal access, but not for AMOE because that triggers standby power per 1009.4.1.
Example: a sprinklered building has a 5th level occupied roof. The roof has pedestal pavers set 8" higher than the main structural floor level. The exit system leads into a lobby landing, which then has a ramp going down 8" to the level of the elevator entrance and the stairwell exit access door. Thus, the MOE on this floor has been "provided with a ramp". Does this meet exception #2 in 1009.2.1?
I know of a developer who wants to provide an elevator for normal access, but not for AMOE because that triggers standby power per 1009.4.1.
In buildings where a required accessible floor or occupied roof is four or more stories above or below a level of exit discharge, not less than one required accessible means of egress shall be an elevator complying with Section 1009.4.
Exceptions:
... 2. In buildings equipped throughout with an automatic sprinkler system installed in accordance with Section 903.3.1.1 or 903.3.1.2, the elevator shall not be required on floors provided with a ramp conforming to the provisions of Section 1012.
Example: a sprinklered building has a 5th level occupied roof. The roof has pedestal pavers set 8" higher than the main structural floor level. The exit system leads into a lobby landing, which then has a ramp going down 8" to the level of the elevator entrance and the stairwell exit access door. Thus, the MOE on this floor has been "provided with a ramp". Does this meet exception #2 in 1009.2.1?