This question / application may have already been discussed. I searched the Forum
archives, but did not find an anything.
The Application: I have an existing Type "B" occ. group setting that is remodeling
some office spaces and an exit corridor. They want to rate the Corridor to a 2 hr. rated
assembly, by installing 2 layers of 5/8" gyp. board on both sides of a corridor wall
nearest the remodeled office spaces. There are existing electrical wires, ..some conduit,
..some Comm. wiring and at least 1 - 4 inch pvc pipe penetrating the now, ..2hr. rated
assembly. The RDP designed plans did not address this "thru penetration" of the pvc
piping, because they did not know it was there. The GC has applied gyp. mud around
this existing pvc pipe as a sealant to prevent the passage of flames & smoke.
QUESTION # 1: Is the sealing around this existing 4" pvc pipe; through a 2 hr. rated
corridor, a compliant method of sealing a "thru penetration" (RE: Section 712.3.1.1.,
..in the 2006 Edition of the IBC)?
Any input is greatly appreciated!
.
This question / application may have already been discussed. I searched the Forum
archives, but did not find an anything.
The Application: I have an existing Type "B" occ. group setting that is remodeling
some office spaces and an exit corridor. They want to rate the Corridor to a 2 hr. rated
assembly, by installing 2 layers of 5/8" gyp. board on both sides of a corridor wall
nearest the remodeled office spaces. There are existing electrical wires, ..some conduit,
..some Comm. wiring and at least 1 - 4 inch pvc pipe penetrating the now, ..2hr. rated
assembly. The RDP designed plans did not address this "thru penetration" of the pvc
piping, because they did not know it was there. The GC has applied gyp. mud around
this existing pvc pipe as a sealant to prevent the passage of flames & smoke.
QUESTION # 1: Is the sealing around this existing 4" pvc pipe; through a 2 hr. rated
corridor, a compliant method of sealing a "thru penetration" (RE: Section 712.3.1.1.,
..in the 2006 Edition of the IBC)?
Any input is greatly appreciated!
.