Morphdesigns
Sawhorse
I am working on a large unlimited area building. In Wisconsin, we are using IBC 2015. Per IBC 507, you need a 60' clear open space on all 4 sides. This building is a 1-story and sprinklered. Per IBC 507.2.1, you are allowed reduced open space, down to 40', if you build a 3-hr wall on the unlimited area building, on the side that is face the reduced open space, as long as it does not go less than 40'.
I have a another building on this site, that is at a 30d angle to my unlimited area building. This building is limited in area, is unoccupied, and is not sprinklered. A corner of this building goes into this required 60' clear space by 8'. So I have 16' of wall on one sidewall and 4' of the other endwall, of this second building within this 60' space. I know that one option is putting a masonry 3-hr wall on my unlimited area building, that is facing this 2nd building.
But I am looking into other options. And hoping that other people might have submitted to their local or state AHJ, as a variance to this code standard. I talked to the sprinkler contractor on the job, and he thought that he did a job that they added rows of exterior sprinkler heads, at 10' oc vertically, facing a tank farm, but after looking into it, it was actually a requirement of FM global to do that, and not because of IBC section 507.2.1.
I was hoping that somebody has done something similar and created a variance to go around this? In Wisconsin, we have a variance process that gives alternate opinions to do instead of following the code. If the description is adequate and the state reviewer discusses this with others, and agrees that this alternate option still follows the intent of the code, it will pass. As I have only worked here, I am not sure if other AHJ's have options to do this.
Thanks for the help.
I have a another building on this site, that is at a 30d angle to my unlimited area building. This building is limited in area, is unoccupied, and is not sprinklered. A corner of this building goes into this required 60' clear space by 8'. So I have 16' of wall on one sidewall and 4' of the other endwall, of this second building within this 60' space. I know that one option is putting a masonry 3-hr wall on my unlimited area building, that is facing this 2nd building.
But I am looking into other options. And hoping that other people might have submitted to their local or state AHJ, as a variance to this code standard. I talked to the sprinkler contractor on the job, and he thought that he did a job that they added rows of exterior sprinkler heads, at 10' oc vertically, facing a tank farm, but after looking into it, it was actually a requirement of FM global to do that, and not because of IBC section 507.2.1.
I was hoping that somebody has done something similar and created a variance to go around this? In Wisconsin, we have a variance process that gives alternate opinions to do instead of following the code. If the description is adequate and the state reviewer discusses this with others, and agrees that this alternate option still follows the intent of the code, it will pass. As I have only worked here, I am not sure if other AHJ's have options to do this.
Thanks for the help.