chris kennedy said:
4/0 to sprinkler pipe?
I'll 2nd that question. Will there be at domestic water line too and not enough info to determine wire size to those unless the disco has built in jumper wires from the lugs to the main ocpd and/or you know what size wires the poco will pull. If that 4/0 is copper it will be overkill anyway.

so other than ensuring both water services are bonded, looks good. God rods not even needed. Still need inter system bonding terminal though.
 
Thanks Guys!.....these guys have been a handfull so far....they got the footings in the ground before I got here and never hit the rebar (250.50) at the State level, they have decided we don't make people jackhammer (so therefore they wll never learn)....Domestic water is all plastic, as well as most of the sprinkler Which might be why they are showing rods(?)
 