Do the interior finish requirements of section 1209.2.2 apply to a small, common-use bathroom? I suggest not.
Section 1209.2.2 of the '18 IBC requires a smooth, hard, nonabsorbent surface on walls and partitions within 2 feet of a water closet. But it also provides an exception for "toilet rooms that are not accessible to the public and that have not more than one water closet".
This section is not explicit in regards to "Common Use" areas, although I believe it is inferred because Public Use is defined separately. I equate "not accessible to the public" as meaning for anything other than Public Use. A common-use area is by definition not a public-use area.
I also note the Chapter 12 summary provided in the 2009 version of IBC in the chapter Effective Use of the IBC, which included the phrase "to resist water damage.... where water is frequently in use". A Public Use toilet area would would have a very different usage frequency compared to a Common Use one.
From this I conclude that the interior finish requirements of 1209.2.2 do not apply to a wall in a Common Use bathroom with only one water closet.
Does this make sense?
Section 1209.2.2 of the '18 IBC requires a smooth, hard, nonabsorbent surface on walls and partitions within 2 feet of a water closet. But it also provides an exception for "toilet rooms that are not accessible to the public and that have not more than one water closet".
This section is not explicit in regards to "Common Use" areas, although I believe it is inferred because Public Use is defined separately. I equate "not accessible to the public" as meaning for anything other than Public Use. A common-use area is by definition not a public-use area.
I also note the Chapter 12 summary provided in the 2009 version of IBC in the chapter Effective Use of the IBC, which included the phrase "to resist water damage.... where water is frequently in use". A Public Use toilet area would would have a very different usage frequency compared to a Common Use one.
From this I conclude that the interior finish requirements of 1209.2.2 do not apply to a wall in a Common Use bathroom with only one water closet.
Does this make sense?