Yikes
SAWHORSE
An ESS (battery storage) room is located on the first floor of a 3B apartment building with an apartment unit above it. The floor/ceiling assembly is 2-hour rated per 2022 Calif Fire Code 1207.7.4.2. The apartment will have plumbing waste lines going across the underside of this floor/ceiling assembly.
Q1: Do I need a second dropped ceiling to separate the pipes from the ESS space? CEC 100.26(E) says that "dedicated electrical space" separation applies specifically as follows: "All switchboards, switchgear, panelboards and motor control devices shall be located in dedicated spaces to protect from damage." Batteries are not any of those devices.
Q2: If the answer to Q1 is "yes", then does the dropped ceiling - - which creates an interstitial space / area for the drainpipes - - need to have the 2 hour rating? 2022 CFC 1207.7.4.2 says"...rooms and areas containing ESS shall be separated from other areas in the building". Is the soffited interstitial plumbing space between the ESS room and the apartment floor assembly considered "other area" requiring 2-hour separation?
Q1: Do I need a second dropped ceiling to separate the pipes from the ESS space? CEC 100.26(E) says that "dedicated electrical space" separation applies specifically as follows: "All switchboards, switchgear, panelboards and motor control devices shall be located in dedicated spaces to protect from damage." Batteries are not any of those devices.
Q2: If the answer to Q1 is "yes", then does the dropped ceiling - - which creates an interstitial space / area for the drainpipes - - need to have the 2 hour rating? 2022 CFC 1207.7.4.2 says"...rooms and areas containing ESS shall be separated from other areas in the building". Is the soffited interstitial plumbing space between the ESS room and the apartment floor assembly considered "other area" requiring 2-hour separation?