Are these permitted as cleanouts?

Sifu

SAWHORSE
Joined
Sep 3, 2011
Messages
3,325
The opening is not the same size as the pipe it serves...so will it be acceptable as a cleanout in a floor drain?
1627679418952.png
 
Looks like it is possibly manufactured by Sioux Chief. Image is linked.

Only two units have an IAPMO listing. Listing is available from IAPMO (linked).

1627681675534.png
 
California Plumbing Code allows a 2" pipe to have a 1.5" cleanout.
 