HERE ARE THE FACTS:
AREA CALCULATIONS:
1,674 SF - EXISTING CONDITIONED B BUSINESS
4,366 SF - EXISTING CONDITIONED F-1 FACTORY
10,038 SF - NEW CONDITIONED S-1 STORAGE
1,420 SF - NEW UNCONDITIONED COVERED STORAGE
17,498 SF - TOTAL
BUILDING OCCUPANCY CLASSIFICATION:
MIXED OCCUPANCY
GROUP B, (SECTION 304.1) - 1,674 SF
GROUP F- 1 (SECTION 306.2) - 4,366 SF
GROUP S-1, (SECTION 311.2) - 9,950 SF
CONSTRUCTION TYPE:
TYPE IIB, NON-COMBUSTIBLE (UN-SPRINKLERED, UNPROTECTED), (SECTION 601)
ALLOWABLE HEIGHTS AND AREAS:
SECTION 503.1 REFERS TO SECTIONS 504 AND 506 FOR BUILDING HEIGHT, NUMBER OF STORIES, AND AREA.
HEIGHT B, F, S 55’ (TABLE 504.3)
NUMBER OF STORES B, F-1, S-1 2 STORIES MOST RESTRICTIVE (TABLE 504.4)
AREA ARE B, F-1, S-1. 15,500 SF MOST RESTRICTIVE (TABLE 506.2)
AREA INCREASE (SECTION 506.3.3)
If=(F/P-.25)W/30 (CALCULATED w IS 52, 30 MAX)
If=(632.125/632.125-.25)30/30 = .75 = 75%
INCREASE 15,500+(15,500X.75) = 27,125 SF
ACTUAL BUILDING HEIGHT = 23'
ACTUAL BUILDING NUMBER OF STORIES = 1
ACTUAL BUILDING AREA = 17,498
BUILDING OFFICIAL SAYS:
"1) To proceed building an addition exceeding 15,500 (F1) most stringent of the mixed uses without a fire sprinkler and fire alarm system, a 3 hour fire wall will be required between the F1 and S1 occupancies with 3-hour rated doors, self closing in accordance with Section 707.3.10 of the IBC, 2018 Edition. This item needs clarification.
2) If you decide to sprinkler and alarm the building, a sprinkler and fire alarm package is required to be submitted to an approved third party for review and approval. This must be done prior to the installation of these systems. Separate permits are required."
QUESTION:
Doesn't the area increase apply to the max un-sprinklered area from 15,500 to 27,125? My Owner doesn't want to install a sprinkler system and also doesn't want to separate the F-1 from the S-1 with a 3-hour fire wall.
AREA CALCULATIONS:
1,674 SF - EXISTING CONDITIONED B BUSINESS
4,366 SF - EXISTING CONDITIONED F-1 FACTORY
10,038 SF - NEW CONDITIONED S-1 STORAGE
1,420 SF - NEW UNCONDITIONED COVERED STORAGE
17,498 SF - TOTAL
BUILDING OCCUPANCY CLASSIFICATION:
MIXED OCCUPANCY
GROUP B, (SECTION 304.1) - 1,674 SF
GROUP F- 1 (SECTION 306.2) - 4,366 SF
GROUP S-1, (SECTION 311.2) - 9,950 SF
CONSTRUCTION TYPE:
TYPE IIB, NON-COMBUSTIBLE (UN-SPRINKLERED, UNPROTECTED), (SECTION 601)
ALLOWABLE HEIGHTS AND AREAS:
SECTION 503.1 REFERS TO SECTIONS 504 AND 506 FOR BUILDING HEIGHT, NUMBER OF STORIES, AND AREA.
HEIGHT B, F, S 55’ (TABLE 504.3)
NUMBER OF STORES B, F-1, S-1 2 STORIES MOST RESTRICTIVE (TABLE 504.4)
AREA ARE B, F-1, S-1. 15,500 SF MOST RESTRICTIVE (TABLE 506.2)
AREA INCREASE (SECTION 506.3.3)
If=(F/P-.25)W/30 (CALCULATED w IS 52, 30 MAX)
If=(632.125/632.125-.25)30/30 = .75 = 75%
INCREASE 15,500+(15,500X.75) = 27,125 SF
ACTUAL BUILDING HEIGHT = 23'
ACTUAL BUILDING NUMBER OF STORIES = 1
ACTUAL BUILDING AREA = 17,498
BUILDING OFFICIAL SAYS:
"1) To proceed building an addition exceeding 15,500 (F1) most stringent of the mixed uses without a fire sprinkler and fire alarm system, a 3 hour fire wall will be required between the F1 and S1 occupancies with 3-hour rated doors, self closing in accordance with Section 707.3.10 of the IBC, 2018 Edition. This item needs clarification.
2) If you decide to sprinkler and alarm the building, a sprinkler and fire alarm package is required to be submitted to an approved third party for review and approval. This must be done prior to the installation of these systems. Separate permits are required."
QUESTION:
Doesn't the area increase apply to the max un-sprinklered area from 15,500 to 27,125? My Owner doesn't want to install a sprinkler system and also doesn't want to separate the F-1 from the S-1 with a 3-hour fire wall.