9.15.3.4. Basic Footing Widths and Areas
(2) Where the supported joist span exceeds 4.9 m in buildings with light wood frame walls, floors and roofs, footing
widths shall be determined according to,
(a) Section 4.2., or
(b) the following formula:
W = w • [ Σ sjs / (storeys • 4.9)]
(3) Where a foundation rests on gravel, sand or silt in which the water table level is less than the width of the footings
below the bearing surface,
(b) the footing area for columns shall be not less than twice the area required by Sentences (1) and (2), and
Article 9.15.3.7.
Questions:
1. Is footing area of columns permitted to use the formula of (2)(b) to calculate when supported joist span exceeding 4.9 m? (Note: 9.15.3.4.((3)(b) references 9.15.3.4.(2) for footing area)
2. In reality, columns would support beams and beams support joists, while the beam span would be the column spacing as in the table 9.15.3.4, is this understanding correct?
Article 9.15.3.7.
Questions: