mshields
Silver Member
517.26 indicates that the "essential electrical system shall meet the requirements of Art 700 except as amedned by Article 517.
This makes clear that not only the Emergency branches of a hospital system need to meet 0.01 selectivity but also the Equipment Branch.
I just wanted to make sure that there wasn't written somewhere in 517 something to exempt the Equipment branch from this very stringent, difficult to meet selectivity requirement?
This makes clear that not only the Emergency branches of a hospital system need to meet 0.01 selectivity but also the Equipment Branch.
I just wanted to make sure that there wasn't written somewhere in 517 something to exempt the Equipment branch from this very stringent, difficult to meet selectivity requirement?