• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

As-Builts

cheyer

Registered User
Joined
Nov 3, 2009
Messages
172
Location
Sunny California..well mostly..
When are you guys requesting fire sprinkler/fire alarm as-builts to be resubmitted to the plan checker for review?

A. When common sense dictates?

B. Only when major deviations from approved plans?

C. It doesn't matter....if it's not on the approved plans, resubmit?
 
It depends upon how tight they did the hydraulic calculations. If they leave no safety factor and had to add some offsets they should resubmit. If they left a health safety factor and had to make a few field offsets, I generally do not worry about it.
 
for plans if a number of devices are going to be added in the field, yes so it can be reviewed prior to install

hydraulics if there is a problem with them resubmit

a few sprinkler heads need adjusting NO!

this is during plan review

in the field normaly do not require as builts to be submited, because should have been handled during plan review

now during plan review, if there are some changes that are needed, but NO real plan review is needed, may ask for an as built set at the end of the project, so we have something close to what was installed.
 