IMC
602.2.1 Materials exposed within plenums. Except as required
by Sections 602.2.1.1 through 602.2.1.5, materials
exposed within plenums shall be noncombustible or shall
have a flame spread index of not more than 25 and a
smoke-developed index of not more than 50 when tested in
accordance with ASTM E 84.
Exceptions:
1. Rigid and flexible ducts and connectors shall conform
to Section 603.
2. Duct coverings, linings, tape and connectors shall conform
to Sections 603 and 604.
3. This section shall not apply to materials exposed within
plenums in one- and two-family dwellings.
4. This section shall not apply to smoke detectors.
5. Combustible materials enclosed in approved gypsum
board assemblies or enclosed in materials listed and
labeled for such application.
602.2.1.1 Wiring. Combustible electrical or electronic
wiring methods and materials, optical fiber cable, and optical
fiber raceway exposed within a plenum shall have a
peak optical density not greater than 0.50, an average optical
density not greater than 0.15, and a flame spread not
greater than 5 feet (1524 mm) when tested in accordance
with NFPA 262. Only type OFNP (plenum rated
nonconductive optical fiber cable) shall be installed in plenum-
rated optical fiber raceways.Wiring, cable, and raceways
addressed in this section shall be listed and labeled
as plenum rated and shall be installed in accordance with
ICC Electrical Code.