I am working on a real estate office. There is a 648 sf training room and a 555 sf break room, the other 6200 sf is office use . The reviewer wants me to put panic hardware on all of the exit/ exit access doors. See below for permit comment and my response. He came back with the exact same comment a second time.
Reviewer: There are over 50 people in the assembly occupancies in the space, please provide panic hardware on the egress doors from the suite.
Response: I respectfully disagree with your interpretation of this code. IBC section 303.2.1 (2) A room or space used for assembly purposes that is less than 750 sf in area and accessory to another occupancy shall be classified as Group B occupancy or as part of that occupancy. Further, IBC 1010.2.9 Swinging doors serving a Group H occupancy and swinging doors serving rooms or spaces with an occupant load of 50 or more in a Group A or E occupancy shall not be provided with a latch or lock other than panic hardware or fire exit hardware. As all of these gathering spaces are less than 750 sf, they are considered a B occupancy, not an A or an E. Training room 337 is 648 sf and the break room is 555 sf.
Reviewer: There are over 50 people in the assembly occupancies in the space, please provide panic hardware on the egress doors from the suite.
Response: I respectfully disagree with your interpretation of this code. IBC section 303.2.1 (2) A room or space used for assembly purposes that is less than 750 sf in area and accessory to another occupancy shall be classified as Group B occupancy or as part of that occupancy. Further, IBC 1010.2.9 Swinging doors serving a Group H occupancy and swinging doors serving rooms or spaces with an occupant load of 50 or more in a Group A or E occupancy shall not be provided with a latch or lock other than panic hardware or fire exit hardware. As all of these gathering spaces are less than 750 sf, they are considered a B occupancy, not an A or an E. Training room 337 is 648 sf and the break room is 555 sf.