Bearing wall, Type IIIB. Table 601 requires 2 hour. Separation is over 30'.
704.5, 2006 IBC allows fire resistive construction on inside only.
I would like to know if the group requires a specific assembly number for an asymmetrical fire resistive wall, or if you would allow (as I would), a typical 2 hour listed symmetrical assembly, but with the rated materials only on the inside.
Thanks