*Reference 2018 IBC*
Situation: Vertical opening with exit access stair is protected in accordance with condition #4 of 1019.3:
Another vertical opening is in level 2 which connects Level 1 to Level 2. The two openings are a distance of 12 feet apart.
Drawings are not available since project is in development and not made public
Question: Is my code approach solid?
Code Approach: Can't I protect vertical openings with any of the 16 options available under 712.1. I have one opening protected in accordance with 712.1.12 Exit access stairways and ramps. The second opening (two openings in Level 2) will be protected in accordance with 712.1.7 Atriums. In section 403 it permits a two-story opening without smoke control (404.5) and without protection from adjoining spaces by fire barrier (404.6 #4). I have satisfied all methods of protection I believe and do not need to protect the second opening without a stair from the opening with the stair. The code does not mention that openings X feet apart shall be considered a single opening.
Also for consideration: The stair is huge so the opening is greater than 1,000 square feet. NFPA 13 Section 8.15.4.4 Large Openings states that closely spaced sprinklers and draft stops are not required. Further evidence I wouldn't need to protect the smaller opening in Level 2.
Situation: Vertical opening with exit access stair is protected in accordance with condition #4 of 1019.3:
- Sprinklered building
- Area of opening is no more than 2x the projected area of stairs
- Draft Curtain and closely spaced sprinklers
- Connects 4 stories (Level 1-Level 4)
Another vertical opening is in level 2 which connects Level 1 to Level 2. The two openings are a distance of 12 feet apart.
Drawings are not available since project is in development and not made public
Question: Is my code approach solid?
Code Approach: Can't I protect vertical openings with any of the 16 options available under 712.1. I have one opening protected in accordance with 712.1.12 Exit access stairways and ramps. The second opening (two openings in Level 2) will be protected in accordance with 712.1.7 Atriums. In section 403 it permits a two-story opening without smoke control (404.5) and without protection from adjoining spaces by fire barrier (404.6 #4). I have satisfied all methods of protection I believe and do not need to protect the second opening without a stair from the opening with the stair. The code does not mention that openings X feet apart shall be considered a single opening.
Also for consideration: The stair is huge so the opening is greater than 1,000 square feet. NFPA 13 Section 8.15.4.4 Large Openings states that closely spaced sprinklers and draft stops are not required. Further evidence I wouldn't need to protect the smaller opening in Level 2.