Working on a small medical office renovation (Class B, type IIB construction). The office is two stories, each being around 2,000sf (below sprinkler requirement). The existing building is not sprinklered, but the lobby/entrance/waiting area is. The waiting area has a 2 story atrium space, there is no stair within it (stair is located elsewhere), but it opens up to Level 2 with a railing separation. Looking at Section 404.3 it states that the area of a building adjacent or above the atrium need not be sprinklered provided that portion of the building is separated from the atrium portion by not less than 2-hour fire barrier. The way the walls for the two levels layout we need to go through hoops to continue the rating up to roof deck.
Looking at 712.1.9 (5), it states that a vertical opening connecting 2 stories is permitted if it isn't open to a corridor on non-sprinklered floors, but looking at this I am not sure if this applies to us. As mentioned above the area around the atrium is sprinklered, but the rest of the floor is not sprinklered. The non-sprinklered area is separated by a wall/door, not sure what rating. Without knowing this is that enough, or would we need to go by 404 and add the 2 hour fire barrier?
Looking at 712.1.9 (5), it states that a vertical opening connecting 2 stories is permitted if it isn't open to a corridor on non-sprinklered floors, but looking at this I am not sure if this applies to us. As mentioned above the area around the atrium is sprinklered, but the rest of the floor is not sprinklered. The non-sprinklered area is separated by a wall/door, not sure what rating. Without knowing this is that enough, or would we need to go by 404 and add the 2 hour fire barrier?