• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Automatic Clothes Washer Waste Connection

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,028
Location
Somewhere Too Hot & Humid
There seems to be a big difference between Commercial and Residential requirements for an Automatic Clothes Washing Machine (comm) and a Clothes Washing Machine (res).

While the plumbing code for commercial (406.2) requires that:

The waste from an automatic clothes washer shall discharge through an air break into a standpipe in accordance with Section 802.3.3 or into a laundry sink. The trap and fixture drain for an automatic clothes washer standpipe shall be not less than 2 inches (51 mm) in diameter. The fixture drain for the standpipe serving an automatic clothes washer shall connect to a 3-inch (76 mm) or larger diameter fixture branch or stack. Automatic clothes washers that discharge by gravity shall be permitted to drain to a waste receptor or an approved trench drain.

Meanwhile, the residential code simply states:

The discharge from a clothes washing machine shall be through an air break.

The commercial code has more requirements since you must connect the fixture drain to a 3" or larger fixture branch or stack. The residential code does not have that requirement.


Do you think this is unnecessary language due to standard practices? How often do you see a 2" fixture drain going into another 2" or 2-1/2" branch anyway?
 
I’d say the transition into a 3” branch or stack for commercial is necessary, commercial usage is typically higher hence the use of commercial equipment vs residential equipment. I can also assume the discharge volume of a commercial washer is greater vs residential..
 
So how long is too long for a fixture drain before you make them change it over to 3"?
CPC (or UPC) 804.1 - Trap must be not more than 18" above the floor, and shall not be installed below the floor. It won't allow a long distance if you consider a pipe slope for drain.
 