B, S-1 and M separations w/sprinklers

Hyrax4978

REGISTERED
Joined
Nov 28, 2016
Messages
245
Location
Hartford, CT
I am working on a project inherited from someone else. Needless to say i can not just call them to ask the question. LOL
Its a 30,000 SF new construction consisting of B, S-1 and M fully sprinklered. The previous designer had a 1 hr separation between the uses. I don't see where this is required based on "N" listed on the separation of occupancies and sprinklering the building to accommodate Chapter 9.
Am I missing something?
 
Don't sound like it. Some people hang on to old codes, and some people over design, which is nice sometimes.
 
I am working on a project inherited from someone else. Needless to say i can not just call them to ask the question. LOL
Its a 30,000 SF new construction consisting of B, S-1 and M fully sprinklered. The previous designer had a 1 hr separation between the uses. I don't see where this is required based on "N" listed on the separation of occupancies and sprinklering the building to accommodate Chapter 9.
Am I missing something?
no separation is required per section 508.4 of the CSBC
 
So if the S1 does not need to be separated from the B or M uses. How does the storage room over 100 SF play in. One could argue that would trigger the rating at the S1 area.
 
I see the building is fully sprinklered. Under the incidental use provisions a storage room over 100sf not needs to be ‘construction capable of resisting the passage of smoke” when sprinklers are in play. Has to be 1 hour rated with no sprinklers.
 