I just got the evaluation cals for a change of occupancy using IBC 3412 form the desiger and it works without sprinklers but the problem is this section:
IBC 3412.3.2 Compliance with other codes. Buildings that are evaluated in accordance with this section shall comply with the International Fire Code and the International Property Maintenance Code.
So in the IFC:
IFC 102.3 Change of use or occupancy. No change shall be made in the use or occupancy of any structure that would place the structure in a different division of the same group or occupancy or in a different group of occupancies, unless such structure is made to comply with the requirements of this code and the International Building Code. Subject to the approval of the fire code official, the use or occupancy of an existing structure shall be allowed to be changed and the structure is allowed to be occupied for purposes in other groups without conforming to all the requirements of this code and the International Building Code for those groups, provided the new or proposed use is less hazardous, based on life and fire risk, than the existing use.
IFC 903.2.8 Group R. An automatic sprinkler system installed in accordance with Section 903.3 shall be provided throughout all buildings with a Group R fire area.
The designer said he used IBC 3412 in other areas and got the ok from the BCO's to do this without sprinklers. Does anyone know some where in the IFC that this can be done?
I dont understand how the IBC can allow R-2 without sprionklers by using IBC 3412 but the IFC doesn't? I thought they where supposed to be compatible?
IBC 3412.3.2 Compliance with other codes. Buildings that are evaluated in accordance with this section shall comply with the International Fire Code and the International Property Maintenance Code.
So in the IFC:
IFC 102.3 Change of use or occupancy. No change shall be made in the use or occupancy of any structure that would place the structure in a different division of the same group or occupancy or in a different group of occupancies, unless such structure is made to comply with the requirements of this code and the International Building Code. Subject to the approval of the fire code official, the use or occupancy of an existing structure shall be allowed to be changed and the structure is allowed to be occupied for purposes in other groups without conforming to all the requirements of this code and the International Building Code for those groups, provided the new or proposed use is less hazardous, based on life and fire risk, than the existing use.
IFC 903.2.8 Group R. An automatic sprinkler system installed in accordance with Section 903.3 shall be provided throughout all buildings with a Group R fire area.
The designer said he used IBC 3412 in other areas and got the ok from the BCO's to do this without sprinklers. Does anyone know some where in the IFC that this can be done?
I dont understand how the IBC can allow R-2 without sprionklers by using IBC 3412 but the IFC doesn't? I thought they where supposed to be compatible?