• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

Bakery occupancy classification

rth

Bronze Member
Joined
Nov 26, 2012
Messages
39
Location
Central MS
I see bakeries are under F-1 but what about a small bakery that just sells to walk ins? I'm told this would be classified as a business but would like to know where to find this in writing.

2006 IFC adopted

Thanks
 
Retaraunt A2...less than 50 occupants B

303.1.1 Small buildings and tenant spaces.

A building or tenant space used for assembly purposes with an occupant load of less than 50 persons shall be classified as a Group B occupancy.
 
steveray said:
Retaraunt A2...less than 50 occupants B 303.1.1 Small buildings and tenant spaces.

A building or tenant space used for assembly purposes with an occupant load of less than 50 persons shall be classified as a Group B occupancy.
If no seating, not a restaurant . sales only, M
 
So the business is not going to do anything to encourage customers to stay eat and buy any more stuff

If so M it is
 
cda said:
So the business is not going to do anything to encourage customers to stay eat and buy any more stuffIf so M it is
I don't know that we do not have all the information, do we ever?
 
In the bigger scheme of life we are merely cogs in the wheel of life, and so is this pondering, a cog in the evolution of the code of life
 
Small neighborhood bakeries should be B or M. F-1 would be for large BAKERIES that send out baked goods by the truckload.
 
Paul Sweet said:
Small neighborhood bakeries should be B or M. F-1 would be for large BAKERIES that send out baked goods by the truckload.
Agree just like print shop vs printing plant.

800 sq ft bakery with one double decker oven and 2 display cases that buys sugar and flour by the sack and makes custom cakes, cupcakes, and cookies is a B. 811,000 sq ft bakery with multiple continuous production lines for cookies and crackers with dual rail spurs for bringing in the flour, sugar, and shortning by multiple railcar lot with 70 ft high automated rack storage for finished goods F-1/S-1. These two examples are about 4 miles apart in our county.
 
Last edited by a moderator:
Are there much difference in code requirements for a B or M , for small buildings???
 
Thanks fellas, given the square footage looks like the occupant load will be over 50 so A-2 it is.

Curveball - upstairs attic is office space so now it has to be sprinkled top to bottom, right? 903.2.1.2
 
rth said:
Thanks fellas, given the square footage looks like the occupant load will be over 50 so A-2 it is. Curveball - upstairs attic is office space so now it has to be sprinkled top to bottom, right? 903.2.1.2
Are you using the entire sq ft to make that call or just where customers will be
 