Townhouse built before there was a requirement for egress back when we had NO codes. Owner wants to finish the basement. Does egress apply if it is not a bedroom?
What is the new use? Or if you prefer, what was the old use?fatboy said:An unfinished basement turning into a finished space is a change of use. New EERO in compliance with the adopted code. "When it was built" may have been in the 50's when EERO's were unheard of, and we have these cute litlle 18" X 30" windows 6 feet of the floor. Not going to fly here.
Does it matter if the basement is finished or not? The EERO isn't required because of a heightened level of use. All basements are required to have an EERO. The problem here is a basement that is legal without an EERO and unless bedrooms are added, there is no code compliant way to require an EERO.EMERGENCY ESCAPE AND RESCUE OPENINGSR310.1 Emergency escape and rescue required. Basements,
habitable attics and every sleeping room shall have at least one
operable emergency escape and rescue opening. Where basements
contain one or more sleeping rooms, emergency egress
and rescue openings shall be required in each sleeping room.
Where emergency escape and rescue openings are provided
they shall have a sill height of not more than 44 inches (1118
mm) above the floor. Where a door opening having a threshold
below the adjacent ground elevation serves as an emergency
escape and rescue opening and is provided with a bulkhead
enclosure, the bulkhead enclosure shall comply with Section
R310.3. The net clear opening dimensions required by this section
shall be obtained by the normal operation of the emergency
escape and rescue opening from the inside. Emergency
escape and rescue openings with a finished sill height belowthe
adjacent ground elevation shall be provided with a window
well in accordance with Section R310.2. Emergency escape
and rescue openings shall open directly into a public way, or to
a yard or court that opens to a public way.
Exception: Basements used only to house mechanical
equipment and not exceeding total floor area of 200 square
feet (18.58 m2).
The 2006 removed the requirement that the basement have a habitable space. Under todays code all basements have at least one EERO at time of construction. Our policy on older homes is if the basement was permitted as "unfinished" in other words no habitable space then the basement does not need an EERO. However under the older codes when a habitable space is placed within a basement then an EERO was required so it is not a change of use per say it is the fact that a habitable space if being established in the basement. As i pointed out above the BO can require one based on R102.7Yankee said:I wonder what code year basements were required to have EERO?
Actually, it will now be used a lot more then when the basement was a root cellar.fatboy said:The use of the stair has not changed, it functions exactly the same as it did before.
State level modification here...(I think they will go to about 6'2" on stairs and beam) we are still 2003 based.....only gets an EERO if it gets a bedroom....and zoning does not allow those in a basement.....(Long stupid story....)rktect 1 said:If you have an existing home built in 1910, and the floor to ceiling height in the basement is 6'-4" because it was used as mechanical room or root cellar, and someone wants to finish it out, do you also make them lower the basement floor or raise the home several inches? Or tell them they can not finish it out?