A hospital lab wants to have two 55 gallon drums of a flammable liquid in their basement lab. (basement is a B occupancy) Using the 2009 IFC section 3404.3.5.1 states if sprinklered in accordance with 9 you may store up to the open amounts of table 2703.1.1(1). This would be 30 gallons for a Class I-b + I-c. The commentary also mentions the increases for the table notes is allowed.
Is 60 gallons of class Ib and Ic per control area allowed in this sprinklered basement, with table 2703.8.3.2 allowing 3 control areas with 1-hour barriers?
Can they dispense out of these drums into 1 gallon containers in the basement? 3405.3.7.2 just says you cannot dispense out of basement of H-2 or H3. Can you then dispense in basement of other occupancies? Can they have a doubling for FL cabinets?
Is 60 gallons of class Ib and Ic per control area allowed in this sprinklered basement, with table 2703.8.3.2 allowing 3 control areas with 1-hour barriers?
Can they dispense out of these drums into 1 gallon containers in the basement? 3405.3.7.2 just says you cannot dispense out of basement of H-2 or H3. Can you then dispense in basement of other occupancies? Can they have a doubling for FL cabinets?