• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

BBQ Pit Under Pavilion

jar546

Forum Coordinator
Joined
Oct 16, 2009
Messages
11,089
Location
Somewhere Too Hot & Humid
2009 IBC applies, the IFC only applies as referenced by the IBC.

Outside BBQ pit under pavilion. We can't find where it is not allowed but trying to figure out if the IFC has something for this situation.
 
I only see:

308.1.4 Open-flame cooking devices. Charcoal burners and other open-flame cooking devices shall not be operated on combustible balconies or within 10 feet (3048 mm) of combustible construction. Exceptions:1. One- and two-family dwellings.2. Where buildings, balconies and decks are protected by an automatic sprinkler system.3. LP-gas cooking devices having LP-gas container with a water capacity not greater than 21/2 pounds [nominal 1 pound (0.454 kg) LP-gas capacity].
So if the canopy and supports for the outdoor pavillion are non-combustible and or 10' from the surface of the BBQ pit it would be compliant.
 