So, there are solutions, just the IRC doesn't make them mandatory.The IRC allows recirculator hoods, and hoods are not even a requirement in a SFR.
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
So, there are solutions, just the IRC doesn't make them mandatory.The IRC allows recirculator hoods, and hoods are not even a requirement in a SFR.
Correct.So, there are solutions, just the IRC doesn't make them mandatory.
Slab on grade is inherently difficult since your volume to exposed surface area is so skewed. That why the code is slowly changing to equivalent leakage area. That's the only correct blower door number not ACH50.The hardest home to pass a Blower Door Test is a slab on grade.
Keep in mind that the BDT is measuring the square inches of open gaps to the outside of a home. If I'm running the BDT and you open a window, I can look at my CFM numbers on my manometer and tell you how far open you made that window.
The BDT is based on the volume (cubic Ft) of the entire thermal envelope of the home and the amount of CFM leaving it at -50PA.
Slab on grade has 1/2 the volume of a home with a standard basement, therefore has 1/2 the amount of allowable airflow for the BDT to pass.
Slab on grad also tends to punch the HVAC plenum through the ceiling and turn the ceiling into Swiss cheese with supply registers.
I tell builders when building slab on grade to put a bead of liquid flashing on both sides of the sill-seal foam gasket before the sill-plate is installed. This creates a much better bond and can be the difference between passing and failing. Without doing this method first, caulking around the entire interior perimeter of the home is the only way they've been able pass. This can be very ugly if the floors and baseboard have already been installed.
I often see zero air-sealing where the plenum exits into the attic through the ceiling, and I rarely see the supply resisters properly air-sealed to the floor of the attic. Unsealed flues and AC line-sets are also contributing to failures, in addition to bath-fans, walk-up attic stairs without thermal covers installed, poorly constructed attic hatches, plumbing/HVAC chases from the attic that lead all the way to the basement, and electrical penetrations left unsealed or sealed from the interior of the home not the attic-side.
Can-lights are also neglected often times as far as air-sealing is concerned.
The bond-joist in the basement is definitely one of the biggest sources for air-infiltration in a standard stick build home.
Insulation companies that flash batt the joist-ends and try to use can foam along the sill-plate have a hard time passing at 4<ach@-50Pa.
Some of this has to do with the quality of the framing too. If the drywall isn't sitting flush to the framing, all sorts of gaps happen along the wall-tops in the attic allowing attic air to infiltrate into the open wall cavities while running the BDT.